Working with PeerNest
The BigFix Client includes a new feature named PeerNest, that allows to share binary files among Clients located in the same subnet. The feature is available starting from BigFix Version 9.5 Patch 11.
A practical use case is a branch office connected to the data center through a slow link: with earlier BigFix versions, the suggested configuration required a Relay to be installed in the branch office in order to download and cache large payloads.
With PeerNest, the BigFix Clients can share downloaded binaries and therefore reduce the number of communications going outside of the branch office even if a Relay is not installed locally. In this way, multiple Clients generate on the Relay the download load of a single Client, because only one Client downloads from the Relay and then shares the download with the peers.
Use of PeerNest can help reducing the number of Relays in some complex BigFix deployment scenarios, therefore reducing infrastructural costs.
An introduction video can be found here: https://www.youtube.com/watch?v=tXRX3zlw1aQ.
Enabling PeerNest
To enable the PeerNest feature, set to 1 the following configuration setting on the Client:
_BESClient_PeerNest_Enabled = 1
The Client enables all the PeerNest feature in order to locally optimize the download of binaries.
This configuration setting requires a restart of the Client to be effective.
PeerNest configuration settings
For details about all available settings, see Peer to peer mode.
PeerNest in depth
When multiple Clients are executing actions requiring the prefetch of a binary file, they check with their peers if the file is already cached in the subnet. If the binary was not cached then the Clients can elect one of them as responsible for downloading from the Relay (Figure 1): the peer with the highest priority, among the peers requiring the file, will manage the download; if all peers have the same priority, the computer with the lowest ID will download the file from the Relay. By doing so, for a given action, all files will likely be downloaded from the Relay by the same computer, and so the downloads will be serialized (one file at a time), thus ensuring minimum bandwidth occupation in the link between Relay and computer.
- A will be elected as master as it has the highest priority among the peers requiring the file (A, B, E).
- C and D do not require the file, so even if D has higher priority than A, D is not involved in the master election process.
Figure 1: Master election

As soon as the elected master (A) starts downloading the file from the Relay (Figure 2) it notifies the other peers that there is a download in progress, so they wait for it without taking further actions. The master sends periodic notifications about the download.
Figure 2: Download in progress

If the peers did not receive the download in progress message (download failed, Client down, network issue), a new election process is started over and another peer becomes master.
When the elected master finishes the download, it moves the file into the PeerNest cache and notifies the other peers about its availability; the peers interested in the file then start downloading it from master and share it, using the same mechanism (Figure 3). In this way, multiple Clients generate on the Relay the download load of a single Client, because only one Client downloads from the Relay and then shares the download with the peers.
The following figure shows how the peers interested in the file (B, E) start downloading it directly from peer A, instead of downloading it from the Relay. When their download completes, the file is cached to be available for future usage: so the Clients A, B and E will share the downloaded file with C and D.
Figure 3: File sharing

Clients with peer enabled will start up an HTTP Server listening on port 52311 for peer
transfers. Each Client can serve at the same time a maximum of
_BESClient_PeerNest_MaxActiveFileDownloads other peers (default value is
5).
_BESClient_Download_RetryMinutes and
_BESClient_Download_RetryLimit Client settings – with the following
addition: - The peer from which a failed download attempt has occurred gets removed from the memory peer list (unless that peer is the only one in memory), and so the next attempt will be done with another peer.
- If the retry-count reaches the limit, the Client will go to download the file directly from the Relay.
If the Client fails to download the file because the peer that it has tried to connect to is already serving 5 downloads (default case), the retry-count is not increased and the peer is not removed from the memory peer list.
PeerNest behavior for files bigger than the PeerCache size
Starting from Version 10 Patch 2, a new feature allows time optimization for actions that require prefetching of large files. This feature ensures that the peers elected for downloads are those with real ability to store files rather than simply those with highest priority.

In fact, prior to Version 10.0.2, in a PeerNest configuration, when BigFix Clients are performing actions requiring the prefetch of a binary file, they check if the file is already cached in the subnet. If the binary file is not cached yet, the BigFix Clients can elect one of them as responsible for downloading from the BigFix Relay and then sharing the file with the peers. The elected peer is generally the one with the highest priority assigned. If the elected peer does not have enough cache to store the payload, the distribution fails, and all the other peers wait needlessly.
Starting from Version 10 Patch 2, with the
_BESClient_PeerNest_UseNoSpaceDownload setting, you can configure the
PeerNest to elect for downloads only the peers with a cache limit higher than the payload
size. The same option forces the peers with high priority but not enough cache limit in
passive mode. In this way, you avoid that the peers have a useless waiting and the file is
downloaded sequentially. With this option, you also provide the peers with the ability to
download the file directly from the BigFix Relay without waiting for the
other peers that might eventually fail.
Excluding a list of subnets
Starting from Version 10 Patch 4, a new feature allows you to disable the PeerNest mechanism for BigFix Clients connected to a specific subnet.
The devices that use the PeerNest mechanism, send and receive messages using the UDP communication protocol. When you have many devices connected on the same subnet, they share network traffic among themselves. This might cause an excessive consumption of network resources. According to your specific needs, you might want to limit the UDP traffic on some specific network subnets. For example, if you have BigFix Clients running in a VPN infrastructure.
Starting from Version 10 Patch 4, with the
_BESClient_PeerNest_ExcludedSubnetList setting, that contains a list of
subnets (for example: 192.1.77.0/25;192.1.77.129/25), you can exclude from the PeerNest
mechanism the Clients that belong to one of the subnets specified in the list. When a Client
with PeerNest enabled (_BESClient_PeerNest_Enabled = 1) registers with the
BigFix Relay, the new feature
identifies the subnet of the Client and checks if its subnet belongs to this list. If yes,
then the PeerNest mechanism is disabled for the Client.
Moreover, when you need to change the Client subnet, for example when you connect to a VPN, if the new subnet is already included into the Exclusion Subnet List, the P2P mechanism is automatically disabled like shown in the following figure.

Adding/modifying/deleting the value of the new setting requires a restart of the BigFix Client.
Best Practices
A good practice is to assign higher priorities to computers with a better link to the Relay and enough resources to serve the other peers of the subnet (and possibly a steady power supply).
PeerNest requires an increased disk storage space for caching files. The default PeerNest
cache size is 2GB, which is enough for many scenarios; it must be increased in case of
transfer of large files (patch management, software distribution, etc.) in order to fit the
cache. The PeerNest cache is intended as a temporary storage, so usage and lifetime can be
fine tuned with the following parameters:
_BESClient_PeerNest_DownloadsCacheLimitMB,
_BESClient_PeerNest_MinimumDiskFreeMB,
_BESClient_PeerNest_MinimumCacheDays,
_BESClient_PeerNest_MaximumCacheDays.
PeerNest requires UDP (port 52311) communication to be enabled, in order to allow the BigFix Clients to communicate with each other.
It also requires TCP (port 52311) to allow the BigFix Clients to download files from a peer, and the subnet supporting multicasting.
It is recommended to set PeerNest in passive mode (using the
_BESClient_PeerNest_IsPassive configuration setting) on Clients that
cannot open this port or do not want to use additional disk space for caching. Passive
Clients will only download from the other peers but will not share content. The following
figure shows an example of configuration.

Bandwidth Throttling
Clients with peer enabled will start up an HTTP Server; the other peers can connect to it for downloading.
Each Client serving files to the other peers can control the amount of bandwidth allocated
for that purpose. The _BESClient_HTTPServer_ThrottleKBPS setting defines
the total number of kilobytes that the Client gives to all of the peers combined per second
(0 means no limit): if its value is 1000 KB/sec and there are 10 peers downloading
simultaneously, the Client will send data to each at 100 KB/sec (for a total of 1000
KB/sec).
PeerNest behavior when using an external Certificate Authority (CA)
In a subnet where there are Agents using client certificates issued by a certificate authority set by the customer, and Agents using the original BigFix client certificates, the behavior of the PeerNest feature may deviate from what is normally expected, since the former are not able to download files from the latter, and vice versa.
For example, if a prefetch actionscript command targets Agents in the described situation, it may happen that more than one Agent downloads the file from the parent Relay, and that some of the Agents - typically sharing the same type of client certificate - obtain the file with delay.
When using the PeerNest feature in a BigFix deployment where an external certificate authority has been set, it is therefore recommended, where possible, to try to have subnets populated by Agents that share the same type of client certificate.
For details about how to set an external certificate authority in a BigFix deployment, see Configuring the root server with a custom CA.
Troubleshooting scenario 1
On BigFix Clients hosted on an Operating System that has the Internet Protocol version 6 (IPv6) disabled or not configured:
If you want to use the PeerNest feature, you must:
- Set on these Clients the
_BESClient_Comm_IPCommunicationsModeconfiguration setting as follows:_BESClient_Comm_IPCommunicationsMode = OnlyIpv4 - Restart the Clients for the changes to take effect.
Troubleshooting scenario 2
On BigFix Clients that have an
active polling set using the _BESClient_Comm_CommandPollEnable and
_BESClient_Comm_CommandPollIntervalSeconds configuration settings:
If you want to use the PeerNest feature, you must not configure these Clients to be
"passive" PeerNest agents. Do not enable on them the
_BESClient_PeerNest_IsPassive configuration setting. Otherwise, depending on the
timing of the polling, multiple Clients in a subnet can download the same binary, without
sharing it.
Peer-to-Peer (PeerNest) Site Gather
Starting from BigFix 11.0.6, PeerNest can be extended to support site gathering in addition to file downloads. When this capability is enabled, BigFix Clients on the same subnet can obtain complete BigFix sites from neighboring peers instead of individually downloading them from their Relay.
This approach reduces Relay traffic and WAN usage, improves distribution speed within branch offices, and lowers infrastructure load while maintaining version correctness for frequently updated content. When PeerNest Site Gather is enabled, the client modifies the traditional site gathering workflow. Before contacting the Relay, the client sends a multicast UDP request over the local subnet to determine whether another peer already has a newer version of the required site or is currently gathering it. If a peer reports that it has a newer version available, the requesting client gathers the site directly from that peer.
If a peer indicates that it is in the process of gathering the site from the Relay, the requesting client waits for completion and then gathers from that peer. If no peer responds, the standard gather process occurs and the highest-priority client retrieves the site from the Relay. Once the gather completes, the client notifies the subnet so that other peers can retrieve the site locally.
New UDP message types are introduced to support site availability requests, responses, gather-in-progress notifications, and gather-complete notifications. A message type identifier differentiates site gather messages from existing P2P file download messages while preserving backward compatibility.
Clients participating in PeerNest run a local TLS-enabled HTTP server on port 52311. With Site Gather enabled, this server can provide the site FileList and individual site files to requesting peers. All connections use TLS with client certificate authentication. Unlike P2P file downloads, site gather does not use the PeerNest cache. Instead, sites are served directly from the client __BESData directory where gathered content is already stored. PeerNest Site Gather supports External Sites, Custom Sites, and Action Sites, including the Master Action Site and Operator Sites. Mailbox Sites are excluded because they are specific to individual clients and cannot be shared. Before serving a site to peers, the client verifies with its parent Relay or Server that no newer version is available. If a newer version exists upstream, the client does not respond to the peer request, ensuring that frequently updated operational content is not distributed in an outdated state.
During the process, clients transition through logical states that reflect whether they are waiting for responses, gathering content, waiting for another peer to complete gathering, or preparing to gather from a selected peer. Only one client per subnet gathers from the Relay when necessary, based on the existing priority mechanism used by PeerNest file download.
Other clients then retrieve the site from that peer once it becomes available.If gathering from a peer fails, the client retries with another available peer. After four failed attempts, the client falls back to the traditional Relay-based gather process. If a peer is temporarily busy because it is serving the maximum number of concurrent downloads, the client retries later without increasing its failure count. This ensures reliability while preserving the ability to revert to the Relay when required.
PeerNest must already be enabled for file downloads before enabling Site Gather.
_BESClient_PeerNest_EnableGatherEnables P2P site gather functionality. Default value is 0 (disabled)._BESClient_PeerNest_IsPassiveAllows the client to gather from peers but not serve sites. Default value is 0 (disabled).
When _BESClient_PeerNest_EnableGather is set to 1, the
client participates in P2P site gathering. Passive peers can download from others but will
not act as site servers. PeerNest must already be enabled for file downloads before enabling
Site Gather.
The setting _BESClient_PeerNest_EnableGather controls whether site gather
through PeerNest is active and is disabled by default.
The setting _BESClient_PeerNest_IsPassive allows a client to gather from
peers without serving content to others. When enabled, passive peers participate in
requesting content but do not respond to peer requests.
Older clients ignore site gather–specific UDP messages and continue operating using traditional P2P file download behavior. Newer clients process both legacy and updated message formats, allowing mixed-version environments to function correctly. All peer communications use TLS with mutual certificate authentication. Content is served only from controlled client directories, and no additional ports are required beyond the standard PeerNest configuration. By extending PeerNest to support site gathering, organizations can further reduce Relay load, accelerate content propagation within subnets, and improve scalability while maintaining security and content integrity.
For details about these settings, see Peer to peer mode.